I have some racks that will be fed by 208V/20A circuits. These circuits will be conditioned and battery-backed by the facility in which these racks will live. 99% of the devices in the rack will be able to support 208V input, so I plan to use these PDUs.
However, there may be one or two odd devices that will need 110V input. I know that I can use a step-down transformer to provide 110V for these devices, but that seems like overkill for such a small number of devices, plus I don't want to pay extra for the UPS functionality since my power will already be battery-backed.
Any suggestions for something I can use for these one-off 110V devices?
As someone who worked in the hosting/datacenter management world I beg of you,
Don't Do That!
If you require 110V power contact your facility/electrician and have a proper 110V feed run to your rack - most facilities are equipped to provide conditioned UPS/Generator backed power at 110V as well as 208V, and already have equipment in place for situations like yours.
If they don't already have a 110V supply available they'll be able to work with you to provide a stable solution for your power needs.
Adding your own step-down gear introduces a number of problems, not the least of which is added load (electrical, but probably more importantly thermal) for the datacenter infrastructure, and would almost certainly be frowned upon by the DC Operations team (If it isn't you may want to seriously consider new hosting arrangements).
I agree with voretaq7, just install a special 120V circuit (and associated rack PDU) for that load. Alternatively find a dual voltage power supply to replace each el-cheapo power brick you have.
Do NOT use a IEC C14 to NEMA 5-15R cable for that. It'll certainly make the copper connection, BUT it won't step down the voltage. Those cables should be banned, IMHO (but I keep one in my bag, just in case.) They are dangerous in the wrong hands as they are a fire hazard. (Since you are asking this question I assume you know those dangers, but I want others to read this.) Others: ALWAYS check the allowed input voltage. Plug in the wrong thing and you'll cause a fire. Which is NEVER good in a DC.
208V is a 3-phase system. The voltage measured between any two phase conductors will be equal. However, the voltage between any phase voltage and neutral is called the "line voltage." The line voltage is less than the phase voltage by a factor of square root of three or 1.732. So, for a phase voltage of 208 volts, measured from phase to phase, the line voltage will be 120-volts (208/1.732), measured from any phase conductor to neutral. This means, technically it is possible to have a passive adapter cord that will deliver 120V from a 208V circuit. I don't know if this is compliant with code or other safety standards though.