Every summer we have to shut down some equipment due to a combination of outside temperature and high load. The air conditioners just can't keep up. As we cycle in new equipment and cycle out old, it would be nice to know if we are making our cooling problem better or worse. Even better, I'd like to be able to calculate a rough estimate of the amount of cooling we'll need to support our equipment at high load.
Is there any rule of thumb or calculation to determine how much cooling capacity will be required?
Computer room/CRAC/HVAC cooling is typically measured in "tons" (for instance, my company's data centers has 15, 20 and 30 ton cooling units depending on room design). The general rule of thumb formula is:
The number of watts is written on the back of the power supply (and in the server's technical specs). The formula to get from watts to BTUs is:
So, say you have a 500 Watt PSU operating at an estimated 80% capacity. You would need:
OK, so now say you have a data center full of 400 of the same servers using the same PSUs:
This is all back of napkin, but it's surprisingly difficult to get hard and fast rules for this stuff. This is all "tons of cooling", but how you have you machines arranged affects this a lot too. Hot/Cold row design helps a ton. If you get really overloaded, the special cabinets that have duct work in the front door and a heat vacuum in the back can really cram more heat into an area.
This will give you an idea of at least what to look for when picking out HVAC units for server rooms:
http://lavrik.net/index.php?option=com_content&task=view&id=12&Itemid=2