With network cables it is easy. I use velcro-ties, coloured cables, 0U vertical cable organizers from APC on side of the rack -- easy and neat.
However with power cables it was always giving me headaches.
With some of the racks I am using Vertical PDUs from APC (0U) so it's kind of neat as am getting 0.3m/0.5m cables and connecting them to servers which are close to the PDU sockets. It's kind of neat, but it could be better.
With horizontal PDUs it is really bad -- no matter how hard I try there is always few cables that are too long and are hanging loose below the APC.
Eg. http://www.flickr.com/photos/92011471@N00/25695150/ -- this will cause the cables on the bottom to be different length and its going to get quite messy...
What are best practices for power cabling? How do you guys do this so your cables once put in once are neat and you don't have to worry about them for years? Do you also cut them to match right length? Do you use some special organizers? Or maybe you know some tricks like hiding them between the side of the server and rack?
I went through many many posts on SF however most of the are oriented around network cabling and very few are touching slightly on the power problem.
Of course I am talking about having network cables on one side and power cables on the other side.
Any suggestions, recommendations, suggestions much appreciated.
Horizontal PDUs are a mess -- In my experience there's nothing that can be done to make these neat: You can bundle your cables neatly down the side of your rack, but when you get to the PDU they fan out into a rat's nest.
For vertical ("Zero-U") PDUs you can acquire custom-length power cables (they're available from various suppliers, usually in the same assortment of lengths you can get ethernet cables in - 1' 3' 5' 7' 14' etc.). The cables can then be bundled and tucked into the side of the rack the same way you would with ethernet cables - I use velcro ties to hold mine to the side of the rack so they don't trap server exhaust...
Some other tips:
(If you have A/B power you can also use different color power cords to distinguish them - e.g. Black/White)
(If you do not have an in-rack keyboard/mouse it IS necessary - a KVM or IP-KVM is not always an adequate substitute)
(You already seem to be aware of this)
Buy short power cables. In the US, I buy 1-foot and 2-foot cables and run to the vertical Zero-U PDUs located on the left and right sides of the rear of the cabinet, since the power supplies are usually situation on the left or right side of the server chassis (never center).
I don't bother with server cable management brackets since they restrict airflow and have become clumsier over the past few years. I buy a roll of raw velcro to cut into strips as necessary to secure the power cables. If I need to pull a system out, I remove the power cable and slide the system out, leaving the power cable hanging in place.
I think you are spot on for the zero-U PDUs. If you have 3-phase power available, I would install one of these on each side of the rack: http://www.apc.com/products/resource/include/techspec_index.cfm?base_sku=AP7892
(208V output is also available but not with 42 connections).
Then connect each server to the appropriate numbered outlet with short power cables. In fact, you can shorten the .5m cables even further by folding them over and using zip ties. Then connect the left power supply to the left PDU, and right to right. For single power supply servers, just alternate between left and right.
With this method, no power cables are ran down the sides of the rack and you don't interfere with your Ethernet cabling.
I would avoid any horizontal PDUs in the rack because they just get in the way of the rest of your equipment.
Use short power cables and Zero U PDUs.
I used to be a Linux Admin in one of the bigger hospitals here in Amsterdam, they relied on massive ammounts of 1u/4p xen boxes which in normal situations is a nightmare when you dealing with proper cable managment. For the first time ever, I fell in love with HP swing-arm based rackmounts, The arms provide the managment while keeping your flexibility (and unblocked cooling!) in the back.
There is one thing though, they had (hospital/goverment = lots of ISO reqs.) special power cables. I had never seen them before, to bad I forgot the material they where coated it. The good news, they flex as good as CAT6, they have about the same size as CAT6 & they should be able to withstand 90C of heat. The bad news: Appearntly they come by 20,- EUR @ 1,5m. Doable when doing half a rack, but kinda costly when you have a full rack of redundant 1u's ;)
Looking at that picture of yours I can do nothing but salute you, nice job.
I have a similar setup with the same servers, racks and APC PDU's. I recycled all the 6ft and 8ft power cables and bought 1 ft ones (they are actualy about 10" in length). I now have zero extra cable.