I have two of these APC units. They use NEMA L5-30P electrical plugs.
I'm using Kill A Watt EZ devices to measure the Amps used by my servers and other equipment with normal electrical plugs but I can't plug the APC units NEMA L5-30P electrical plugs into the Kill A Watt devices.
Does anyone have a ballpark idea of how many Amps an APC unit like this uses by itself without anything plugged into it?
Looking at the spec, it suggests an Online Thermal Dissipation of 375.00 BTU/hr, which is apparently around 110W. Since any difference in current in and current out must be lost as heat, this should be a good indicator of the current draw of the UPS on it's own:
If you want a more accurate measure, then I can think of two possibilities that might help.
Note that just measuring the current draw of the UPS without load may not give you a very accurate indication of it's current draw under real usage. There will probably be a non linear relationship between power in and power out as total power use changes. It may, for instance, be more efficient in the middle of it's range, getting less efficient at very high or very low power usage. Ideally you should test under both normal and worst case load conditions.
Buy a pair of NEMA L5-30P plug & sockets, plus a socket and plug appropriate for your Kill A Watt EZ device, then make a pair of leads, NEMA plug > normal socket & normal plug > NEMA socket. You can then plug your device in-between. Do be careful about wiring up your live/neutral/earth leads to the correct pins though. Ideally, if you aren't a qualified electrical, you should get one to do this for you.
We have 2 of these exact units and they are wired to 30 amp circuits. So anywhere from 20 - 30 I would say. We also have a 5000 watt Powerware unit that uses 30 amps.